This is called an 'automatic transfer switch', it basically islands your off-grid installation when the power isn't available. As you already mention whether or
by jacquesm 5y ago
This is called an 'automatic transfer switch', it basically islands your off-grid installation when the power isn't available. As you already mention whether or not it is allowed is dependent on where you live. As it was the electrical inspectors in Northern Ontario were very much in bed with the power companies and typically would find all kinds of reasons to persuade renewable energy builders to let it go and rely on grid power. Given the state of some of the homebrew systems I've seen they probably had a point.
Automatic transfer switches were technically allowed but at the time I didn't know of a single installation in Northern Ontario that got a stamp of approval and was allowed to be operated un-attended in grid connected mode.
There is some risk, but this is usually exaggerated, the theory goes that a lineman should be able to disconnect a segment and then it should be idle, requiring all renewable installations down-grid to disable themselves. As a rule this is fully automatic anyway because all of the grid connected inverters that I'm aware of stop working as soon as the grid fails because they use the grid to supply them with phase and frequency information required to function.
But that wasn't good enough, the installation needed to be physically disconnected from the grid, requiring a very large relay and somehow it then had to reconnect if the grid came back on for a specified minimum amount of time (I forgot the details). By the time I had worked all this out I figured since I'm going to be in island mode anyway most of the time I may as well take the shortcut, cut the grid entirely (saving a considerable amount of money in the progress) and invest the difference into a nice genset (which I did, a 5.8KW Kubota diesel).
- Throwawayaerlei 5y agoHere in the US Midwest I recently observed some crews repairing a fault just upstream of me, and the last thing they did before reconnecting to upstream of that fault was disconnecting a set of yellow cables which were obviously grounding the downstream wires.
- brianwawok 5y agoLayers of protection. Laws on what can backfeed into the grid, ground the wires, wear safety gear. No different than in computer science using both a firewall AND salting your password. The more layers, the less likely 1 mistake gets you.
- jacquesm 5y agoExactly. If you want to get fired in a hurry from any utility or large plant: override someone else's lock-out. If they don't beat you into a coma first.
- quickthrowman 5y agoThose are called grounding clusters, sibling comment explains why.
- LorenPechtel 5y agoIt is quite reasonable--the idea is that your local system must not backfeed power even in case of failure. You don't rely on how it should operate, it must be *impossible* for a failure to backfeed. Thus, physical switches. The power company doesn't care what throws the switch, just that it exist.
- PaulDavisThe1st 5y agoThe problem here is that different power suppliers in different locations have different standards here. My 6.6kW array here in rural New Mexico is connected to the grid via an inverter that will, putatively, shutdown if the grid side drops. How does the inverter make it impossible for a failure to happen? How different is this from an automatic transfer switch (which would not be allowed)?
- LorenPechtel 5y agoWhat they usually do is design the inverter to only use line power as the reference to generate the output. No sine wave from the line, the circuit is completely unable to produce an output and thus shuts down even in case of failure.
- cduzz 5y agoWhat was the thinking around diesel vs natural gas? Do you just use heating oil? How do you manage that it has a limited shelf life?
- lepton 5y agoNatural gas is very likely unavailable in remote areas. Usual fuels would be propane or diesel, which can be trucked in.
- tw04 5y agoPeople seem to think Natural Gas just magically makes its way down the lines. NG requires power as well. If power is out for any period of time you lose natural gas soon after due to compression stations going offline unless you happen to be one of the lucky ones who lives off a branch that is self-powered. https://geekprepper.com/how-long-will-natural-gas-last-without-electricity/ https://geekprepper.com/how-long-will-natural-gas-last-witho...
- throwaway0a5e 5y agoThat article is from 2015. The bulk of natural gas infrastructure is self powered these days because declines in gas prices since then have made that a comparatively better option in more places and the natural attrition and upgrade cycle of equipment.
- reaperducer 5y agoI don't think "the bulk" is true. Last year's deadly winter storm in Texas showed that a lot of natural gas infrastructure does indeed rely on electricity.
- throwaway0a5e 5y ago>Last year's deadly winter storm in Texas showed that a lot of natural gas infrastructure does indeed rely on electricity. This is just a lie. A bunch of crap in TX froze up because the physical infrastructure was not designed to operate in those temps. When you're compressing and decompressing gasses moisture becomes ice. Their facilities were not designed to prevent icing in low ambient tempts. They had no problem getting power for the most part. Remember, generators are SOP for pretty much all utilities and doubly so anywhere you might get a hurricane (which is a good chunk of TX).
- bluGill 5y agoIn practice the lineman risk isn't as real as it seems at first. Odds are when the lineman shutdowns a segment, if your system tries to supply power there are enough other people on the segment that you will trip your local overload protection and isolate the grid. I don't blame lineman for not wanting to trust that though. My understanding is their practice is to always short out the line when working on them as that is the only way to be 100% sure it isn't live. (note that linemen work on live lines all the time, but when they need a dead line they ensure it is dead)
- silexia 5y agoMy uncle was a lineman and lost his leg due to this issue.
- jacquesm 5y agoAgreed. But given what I've seen in some off-grid installations I really don't blame them. And I have seen one installation that tried to supply all of Ontario when it didn't go off-line as it should have, that wasn't a really pretty sight. The inverter died quite spectacularly, judging by the scorch marks on the wall above it, all of the magic smoke had definitely gone out of that one.
- beezle 5y agoJust adding from an experience researching solar for a condo development - if you want the fire department to try to save your house, you need to be able to cut the panels off, grid connection or not. Likewise, putting panels on both sides of the roof makes it difficult, if not impossible, to vent a fire through the roof. The figures are ever changing, but the additional weight of many panels can also be a consideration when fighting a fire. Really urge anyone considering adding solar panels on their home to speak with their local fire/ems prior to installation/signing a contract to be sure you know their requirements (and in many places this is still evolving).
- darknavi 5y agoI am not familiar with house fires or how to fight them. > putting panels on both sides of the roof makes it difficult, if not impossible, to vent a fire through the roof. If a fire is bad enough to need to be vented from a hole in the roof, wouldn't the building likely be lost already?
- reaperducer 5y agoEven if the building is lost, the firefighters still want to put it out to keep it from spreading. A few weeks ago, the Mount Charleston Lodge in Las Vegas burned to the ground. Firefighters put most of their effort into saving the surrounding national forest.
- Cerium 5y agoNot in my experience. There was a fire in the third floor unit of a building I was living in (one floor up and one unit over). It was a three floor building, so that was a roof unit. The firefighters cut vent holes and were able to contain the damage to that unit.
- stickfigure 5y agoIf you're building condos, you aren't in a rural area. In my rural area, everyone ground mounts because space is cheap. I'm a volunteer firefighter and so far none of the trainings have mentioned solar (venting roofs yes). But then, we joke that we'll arrive just in time to put out your foundation.
- briffle 5y agoAutomatic Transfer switches are very common in Server Rooms and datacenters where there is a Generator in use. I'm not sure why they are not more common in Solar. I have a parent with a full house generator that also has a Automatic Transfer Switch, its essentially right above the breaker box. the breaker box either gets power from the generator, OR from the power company, never both. When power comes back on, the ATS senses it, and sends a signal to the generator after 30 seconds or so that it is switching over, and to shut down.
- toast0 5y agoGrid tied home solar is usually about economics (and sometimes happy feelings), not reliability. If you want automatic transfer, you need to add storage, and a more complex inverter that can operate in bridge tied and island mode, and that cuts into the economics. You might also need to get more panels to handle projected loads during projected outages, but most net metering tarrifs I've seen won't compensate you if you over generate.
- jacquesm 5y agoI can assure you that reliability factors in heavily in Grid tied home solar.
- Symbiote 5y agoThat must depend on the area. People in the Netherlands or the UK have reliable power anyway, but there are still some home solar installations.
- _ea1k 5y agoThat varies greatly. In my area, the grid is extremely reliable. I rarely see systems that are setup to handle outages as the cost isn't really worth it on its own.
- LorenPechtel 5y agoThis. Normal solar relies on the grid as it's "storage". The economics of solar become very different if you have to provide local storage. This is also why there is an ongoing fight over net metering and in some places solar connections aren't even allowed. So long as solar is a small fraction of the total power it has basically zero effect on the grid. Now, however, there are a lot of solar setups. Look what happens to the grid: The total delivered power drops, but the peak power (when the cloud passes in front of the sun and all those panels quit working) stays the same. They need to spend just as much on generators as before but they aren't selling as much power. Historically, the cost of being able to produce the power has simply been folded into the cost of the power but with the two going out of sync this model no longer applies. Solar gets a substantial hidden subsidy from this, without this subsidy solar is almost never economic. Second, look at what happens when *lots* of homes go solar. Lets say the local substation is delivering 1000A of power to it's area. Lots of panels go up, the combined power is 1500A. Now the substation transformer is being asked to push 500A back up to the distribution wires--and it's probably not built to survive that. Either those substations must be upgraded or the power company simply prohibits the situation from arising the in the first place by not allowing too much solar on any given segment.
- mindslight 5y agoI believe that inverters with integrated transfer switches are more common these days, due to the popularity of battery systems like Powerwall. I was reading the manual for one, and it had both a grid connection (to your main panel), and a "protected power" connection for a subpanel that will remain powered regardless of grid power. They must still have some kind of internal transfer switch (as opposed to double conversion), but I would think as a single listed device with anti-islanding, they would be a lot easier sell to an inspector. Then again that AHJ sounds a bit dodgy ("specified minimum amount of time") so maybe they're still resisting.
- reaperducer 5y agoReminds me of the days when you needed written permission from the telco in order to connect a fax machine or modem to the phone line. I remember standing in line at the local phone company office and explaining to a nice chain-smoking office lady (you could still smoke in windowless offices in those days) what a "modem" was and why I wanted to plug one into their sacred network.
- MichaelZuo 5y agoErr wasn’t that correct in hindsight with robocalls and whatnot becoming prevalent?