4 ms·
Is it because less heat escapes from the boiler or the burning is more efficient?
by flowerbreeze 4y ago
Is it because less heat escapes from the boiler or the burning is more efficient?
- maxerickson 4y agoThe old burner likely achieved ~100% combustion (not sure what you mean by the burning being efficient). As to the other part, yes, less heat is sent up the chimney in modern designs. My boiler is getting pretty old but was sold as 80% efficient. As far as I can tell, the near drop in replacement would be 84 or 85%. Neither is a modern condensing boiler (which I'd have to figure out a new exhaust to switch and probably add active outside air exchange; tempting with the way the current one sucks all the humidity out of the house).
- sokoloff 4y agoThe overall burning cycle is more efficient. Even with tuning, my old boiler was putting out well over 200ppm CO (down from 2500/off-scale when they first tested it). That’s one source of inefficiency of getting BTUs of heat out of the gas and into the water. As a sibling mentioned, it was also sending 450+°F vapor-laden exhaust up the chimney and out the roof. New boiler vents through plastic pipe and extracts so much more of the heat that the exhaust is leaving the boiler at around 150°F with the water vapor largely condensed (at least this time of year) and giving up that latent heat of vaporization to the water incoming to the boiler. Additionally, it pulls combustion air from outside instead of the basement. (If you pull combustion air from the basement an equal amount of outside air must leak into the house to replace it.) New boiler also has a modulating gas valve and can burn in 5 steps between 25K BTU/hr and 149K BTU/hr (from memory, but close enough) to match the space heating demand. The old one was either 0 or 200K BTU/hr. I probably went from 60% to 95% now plus the effects of not pulling millions of cubic feet of outside air in per year. The computer controls on this one (and the ability of the boiler to not just tolerate but encourage condensation) mean I can heat my house at 32°F/0°C with 114°F/45°C supply water temps. Traditional boilers are harmed by acidic condensation so need return temps of 140°F which means supply temps of 160°F. That means hotter rads and pipes and more losses in the piping. As it gets colder, the boiler can compensate (via an outdoor sensor) and increase the flow temp so it’s just enough to heat the house. Based on 114°F flow (about 90-95°F return) being enough for 32°F, I'm virtually certain that I'll be operating in condensing mode (return under 120°F) even on the coldest nights we get here or if not, on all but one or two nights. I have pump controls that can run the pumps for a bit after the zone and burner shuts off to put that (much smaller amount) of trapped heat into the living space rather than leaving it trapped in a massive hunk of cast iron to leak to the boiler room. It’s a lot of small and medium effects.
- sokoloff 4y agoEdit: it’s probably closer to a 1/4 million cubic feet of outside air pulled in for combustion rather than “millions”.
- lscharen 4y agoWe replaced a 25+ year-old propane furnace with a high-efficiency natural gas furnace two years ago. The difference in waste heat is astonishing. The old furnace vented through a vertical chimney vent and the exhaust was so hot that touching the metal pipe would burn your hand. The new furnace is direct vented with PVC pipes and the exhaust outside the house feels barely warm — that’s a lot of additional heat that stays in the house instead of being wasted. Between the cost difference of propane vs natural gas, better efficiency and a programmable thermostat, we easily reduced our fuel bill $$ by 50% with no noticeable change in comfort level. I did not track the difference in therms.
- pandaman 4y agoIn a traditional design boilers/furnace you run hot combustion gases through a heat exchanger (HX) to heat water/air and then into a flue. The problem is that if it cools too much in the HX it can condense in the flue. With the condensate being extremely corrosive it will quickly destroy the flue and can cause all kind of issues from CO poisoning to fires. So the HX is small enough to keep the gases hot in the flue to prevent corrosion. A more complicate design has a big HX and various pumps and fans to drain the condensate and push out the exhaust gases. It uses a PVC flue and drain line to withstand corrosion but at the end you still have moving parts exposed to the acidic condensate and it does not have the service life of a straight metal flue design. That, combined with the higher cost of a condensing heater (because of all the additional pumps and fans and corrosion protection), calls for a careful cost analysis since you need to burn a lot of gas to justify quicker replacement and more service calls for a more expensive unit.