4 ms·
That doesn't address anything I said about costs. And you often can't cool air without removing water vapor, the water condenses whether you want it to or not.
by crazygringo 5y ago
That doesn't address anything I said about costs.
And you often can't cool air without removing water vapor, the water condenses whether you want it to or not.
- sokoloff 5y agoYou appear to have previously to be laboring under the misconception that latent heat (the heat required to condense water in gaseous form into water in liquid form) didn’t exist or that humidity isn’t gaseous water. My comment was directly responsive to whichever of those misconceptions was underlying your comment above. That’s why I gave you the term, in an effort to show you politely that you were wrong enough that the HVAC industry has an entire term specific to this concept and that suggests that it’s more than a rounding error. It appears that you at least now agree that water in gas form is condensing into liquid form (which requires the removal of the heat of vaporization [what science calls it] or the latent heat [what HVAC calls it]).
- crazygringo 5y agoAh ha, thank you! I was indeed under the misperception that latent heat was associated only with evaporation/condensation at high-energy boiling points, not at e.g. room temperature for water. Turns out it's fiendishly difficult to find anything on Google or educational materials about phase changes or latent heat that aren't at a boiling (or freezing) point -- no wonder I was never taught it. (Finally found [1].) But in any case, I finally found them and ran the numbers. The latent heat of water is ~4x that of air, but even on a really hot humid summer day water is only 3% of air by mass, which means in a worst-case common scenario, 11% of energy is going to condensing the water, while 89% is simply cooling the air and (non-condensing) humidity. So if we round, we can say that a heat pump cooling humid summer air rather than drier winter air uses up to around 10% more energy (since winter air has a bit of humidity too), which means heating/cooling are still roughly the same for most purposes. Whereas the commenter I was originally replying to seemed to be suggesting cooling takes 3.5x as much energy, which doesn't seem to match summer/winter energy bills at all. Does that cover it, or is there something else my math is missing? Thanks again. [1] https://en.wikipedia.org/wiki/Latent_heat#Specific_latent_heat_for_condensation_of_water_in_clouds https://en.wikipedia.org/wiki/Latent_heat#Specific_latent_he...
- sokoloff 5y agoI think it’s more than that. (Sorry for the use of “stupid units” here. It’s a lot easier to find the non-SI units for the HVAC applications of these and being an American, it’s easier for me to think in BTUs than calories, kWh, or Joules for HVAC.) It takes (negative) 970 BTU to condense one pound of water from gas to liquid. (That’s the latent heat of vaporization.) It takes -0.24 BTU to cool one pound of mixed air by one degree Fahrenheit. At 90°F, air can hold almost 5% of water vapor in suspension. If the task is to condense out about half the water (from 90% to 45% RH) and cool it from 90°F to 70°F, I think it’s: For every 40 pounds of 90°F/90% RH air that you want to make into comfortable inside air: You condense out 1 pound of water at a cost of sinking 970BTU. It’s slightly less than 1 pound, so generously call it 900BTU of latent heat removal. You then cool 39 pounds of mixed air by delta-T of 20°F: 39 * 20 * .24: 195BTU of cooling required for sensible heat removal. That makes it look to me like over 80% of the heat removal is latent and under 20% is sensible. (Phase change is expensive, but you’re glad for that when you’re sweating in air that’s not 100% RH.) This is tapped out on a phone while traveling, so I’m not staking my life on it, but I think it’s right.
- rootusrootus 5y ago> For every 40 pounds of 90°F/90% RH air that you want to make into comfortable inside air: That's a worst case scenario, though. For one, 90/90 would translate to a 87F dew point -- which is not a record, but it's pretty close, and there's a good chance it would be lethal to unprotected humans. So it does not happen too often, e.g. normal in a place like Phoenix Arizona might be 110F but 20% RH. Second, air conditioning doesn't cool outside air, it cools inside air. So on average it isn't going to have nearly that much water to pull out of the air.
- sokoloff 5y agoTypical house has between 0.5 (quite tight) and 2 air changes per hour. It’s true that the HVAC return air is coming from conditioned space, but it’s also true that that air is frequently exchanged to outside air, meaning it’s going to need to be continually dehumidified. I’ll assume you were kidding about a dew point of 87°F being lethal to unprotected humans. Make the assumptions such that you take 1 pound of water out of 200 pounds of air and (0.5% reduction in water content) and the latent and sensible heat are about equal. Dehumidifying is expensive energy-wise is the point.