2 ms·
> ... I may invest in diesel generator and a 5,000 gallon subterranean tank. I highly recommend propane-fueled gensets. Fuel storage is much less hassle, and p
by mirimir 8y ago
> ... I may invest in diesel generator and a 5,000 gallon subterranean tank.
I highly recommend propane-fueled gensets. Fuel storage is much less hassle, and propane doesn't go bad. You won't get the runtime of a huge diesel tank. But there's often little point in that, because an extended power outage will also take down the telecom infrastructure. As I recall, a ~7kW genset at ~70% capacity went through ~40kg propane per day. That was running well pump, sump pump, refrigerator, CFLs, microwave, fans, and a ~3kW UPS for several computers.
Edit: Make sure to get a UPS that accepts genset power. That usually means full online aka double conversion. And everything must be grounded properly. Plus at least a manual transfer switch, to avoid injuring utility workers.
- driverdan 8y agoDiesel doesn't go bad, it can be stored for long periods of time. It's much cheaper to run a diesel generator than propane since diesel is much more energy dense but costs about the same.
- mirimir 8y agoHow long? For people with decent electrical service, you need the genset for at most several hours, maybe once or twice a year. Your UPS should handle ~30 minutes, which is enough for most interruptions. So your fuel supply needs to be stable on the order of decades. Is diesel stable on that scale? And sure, propane can leak. So you need to check every few months.